Sealed combustion heaters in a garage

 
Post new topic   Reply to topic    Alaska Home Inspectors Forum Index -> Energy Issues
View previous topic :: View next topic  
Author Message
Troy Bloxom
Home Inspector


Joined: 24 Jan 2008
Posts: 14
Location: Eagle River

PostPosted: Sun Feb 17, 2008 11:22 am    Post subject: Sealed combustion heaters in a garage Reply with quote

I inspected a 1983 home in Settlers Bay that had a sealed combustion, gravity direct vent, natural gas, wall mounted heater in the garage. It was installed with the burner at about 8" from the floor. It did draw the combustion air from the exterior.

The question is:
Should it be installed with the burner at 18" because when; not if; the heat exchanger fails it will be a hazard.

We install all the sealed combustion F/A furnaces and boilers up on a stand so what would make this different??
I pulled the information on the unit off the web and nothing is mentioned about elevation installation in a garage. In fact it was promoted as a heater for a garage, right next to the Ferrari in the picture.

I called it as a hazard, and recommended that a ceiling mointed F/A unit heater be installed.

Troy
Back to top
Kevin Jones
Home Inspector


Joined: 01 Feb 2008
Posts: 27
Location: Anchorage

PostPosted: Mon Feb 18, 2008 6:16 pm    Post subject: Reply with quote

Troy the IC words it:

M1307.3 Elevation of ignition source. Appliances having an
ignition source shall be elevated such that the source of ignition
is not less than 18 inches (457 mm) above the floor in garages.
For the purpose of this section, rooms or spaces that are not part
of the living space of a dwelling unit and that communicate
with a private garage through openings shall be considered to
be part of the garage.

It does not differentiate between sealed or open combustion. It is improper to have nay source of ignition within 18 inches of the garage floor. This includes electrical devices (receptacles). Your were correct to call the system out as a potential hazard.
_________________
Kevin D Jones
Quality Home Inspection
AK License #39
ICC Combination Residential Inspector
Level 1 Certifed Thermographer
ASHI Certified Member
Back to top
Display posts from previous:   
Post new topic   Reply to topic    Alaska Home Inspectors Forum Index -> Energy Issues All times are GMT - 8 Hours
Page 1 of 1   

 
  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum

Community Chest


Powered by phpBB
Hosted by FreeForums.org